    GY-87 micropython library
    micropythongy-80lopy4
    32 Posts 4 Posters 5.2k Views 4 Watching
      robert-hh @tttadam
      @tttadam I looked for MPU6050 libraries. What I found is for RasPi, but it should be easy to adapt them by replacing the calls for I2C send and receive.
      About the third sensor HMC5883L. Acording to the data sheet there is no enable pin. The DRDY signal could come from that chip. You should check whether you init the I2C bust at a baudrate <= 400000, because that is the max rate mentioned in the data sheet.
        tttadam @robert-hh
        First of all sorry for the long delay.
        I just checked, and seems like no, the last sensor didn't show up on i2c.scan()
        I checked the documentation and the MPU6050 is has some kind of mode/option, where it's connected to other I2c devices, and gather data from them. Maybe the compass is connected to the mpu6050?
        >>> from machine import I2C
        >>> i2c = I2C(0, I2C.MASTER, baudrate=400000)
        >>> i2c.scan()
        [64, 104, 119]
          robert-hh @tttadam
          @tttadam I justz received a sample of the board that you have linked. Three observations:
          • the HMC5883 does not show up in the i2c.scan(), even if the address is ping'ed.
          • the bmp180 returns nonsense-values.
          • the pull-up resistor values on the board are pretty low,
            effectively 1.1kOhm. I will look tonight into the signals with an oscilloscope to verify the signal quality.
          So all-in-all, the board might just be crap.
            tttadam @robert-hh
            @robert-hh ohhh, I didn't even thought about that. But could be. Can you recommend some other sensor?
            pytrack has built-in gyro. what i need pressure, and compass.
            (The weather ballon will have a camera, and when it took a picture, I would like to know the direction)
              robert-hh @tttadam
              @tttadam So, looking at the device and the wiring it seems clear why the HMC5883 is not visible in the scan: it is connected to the MBU6050 slave interface. Still, according to the MPU6050 data sheet, it should be visible, because at start-up the MPU6050 connects the main I2C interface to the aux interface.
              The I2C signals are fine.
              However, on the board I have the BMP180 is broken. The temperature sensor always returns 229.3°C. At least that helped me to find a signed/unsigned bug in my driver.
                tttadam @robert-hh
                @robert-hh said in GY-87 micropython library:
                BMP180
                I just checked the bmp18. It's seems something off with the altitude...
                (1028 is the current QNH in Budapest)
                >>> bmp.sealevel = 1028
                >>> bmp.altitude
                51.46274
                >>> bmp.pressure
                1021.34
                >>> bmp.temperature
                24.2
                >>> si7021.readTemp()
                22.92749
                >>> my_gps.altitude
                120.3
                So you have any guess how Can I get the compass data?
                  robert-hh @tttadam
                  @tttadam The altitude is calculated from the actual pressure and what you enter as sea level pressure, roughly 8.5m/hPa. You can see it in the python script.
                  The compass chip should be available when the I2C-bus is set to pass-through. I'm trying it at the moment.
                    robert-hh @tttadam
                    @tttadam So I found a way to talk to the compass, with the following sequence:
                    i2c=I2C()
                    i2c.writeto_mem(104, 107, 128) # reset MPU6050
                    i2c.writeto_mem(104, 107, 0) # disable sleep
                    i2c.writeto_mem(104, 55, 2)   # enable I2C passthru
                    i2c.scan()
                    The scan should show you another I2C address. In my case it is 13, which deviates from the HMV5883 data sheet.
                      tttadam @robert-hh
                      @robert-hh It's working for me too! :)
                      Awsome! :)
                      Now I just need to find a correct library for it.
                      I will start with this
                      Can you give me some explonation what happend?
                      What your overall expression of the board?
                        robert-hh @tttadam
                        @tttadam When you do the i2c.scan(), which address is reported for the HMC5883? It puzzles me that my device reports 13 instead of 30, which is the address in all examples.
                        Besides that, I have the impression that in normal operation the HMC5883 is controlled by the MCU6050 for its own purpose. So you might get the information you need through the MCU6050.
                        If you ask me about what I did to find that way: I looked at the circuit, read the data sheets and looked at some code examples for the MCU6050.
                          tttadam @robert-hh
                          This is what I see. So same for me.
                          >>> i2c = I2C(1)
                          >>> i2c.scan()
                          [64, 104, 119]
                          >>> i2c.scan()
                          [13, 64, 104, 119]
                            robert-hh @tttadam
                            @tttadam So let's see if that is a bug or an intended address trabslation (but why?)
                              robert-hh @tttadam
                              @tttadam A short google search gave an answer:
                              The chip in the board is not a HMC5883, but a QMC5883. See https://github.com/nodemcu/nodemcu-firmware/issues/2187
                              The QMC5883 server for the same purpose, but has different programming interface.
                                robert-hh @tttadam
                                @tttadam I found a RasPi driver for the QMC5883 and adapted it to pycom MP:
                                # ported from http://nobytes.blogspot.com/2018/03/qmc5883-magnetic-field-sensor.html
                                import struct
                                from machine import idle
                                class QMC5883:
                                    #Default I2C address
                                    ADDR = 0x0D
                                    #QMC5883 = Register = numbers
                                    X_LSB = 0
                                    X_MSB = 1
                                    Y_LSB = 2
                                    Y_MSB = 3
                                    Z_LSB = 4
                                    Z_MSB = 5
                                    STATUS = 6
                                    T_LSB = 7
                                    T_MSB = 8
                                    CONFIG = 9
                                    CONFIG2 = 10
                                    RESET = 11
                                    CHIP_ID = 13
                                    #Bit values for the STATUS register
                                    STATUS_DRDY = 1
                                    STATUS_OVL = 2
                                    STATUS_DOR = 4
                                    #Oversampling values for the CONFIG register
                                    MC5883L_CONFIG_OS512 = 0b00000000
                                    CONFIG_OS256 = 0b01000000
                                    CONFIG_OS128 = 0b10000000
                                    CONFIG_OS64  = 0b11000000
                                    #Range values for the CONFIG register
                                    CONFIG_2GAUSS = 0b00000000
                                    CONFIG_8GAUSS = 0b00010000
                                    #Rate values for the CONFIG register
                                    CONFIG_10HZ = 0b00000000
                                    CONFIG_50HZ = 0b00000100
                                    CONFIG_100HZ = 0b00001000
                                    CONFIG_200HZ = 0b00001100
                                    #Mode values for the CONFIG register
                                    CONFIG_STANDBY = 0b00000000
                                    CONFIG_CONT = 0b00000001
                                    def __init__(self, i2c):
                                        self.i2c = i2c
                                        self.oversampling = QMC5883.CONFIG_OS64
                                        self.range = QMC5883.CONFIG_2GAUSS
                                        self.rate = QMC5883.CONFIG_100HZ
                                        self.mode = QMC5883.CONFIG_CONT
                                        self.reset()
                                    def reconfig(self):
                                        print("{0:b}".format(self.oversampling | self.range | self.rate | self.mode))
                                        self.i2c.writeto_mem(QMC5883.ADDR, QMC5883.CONFIG, self.oversampling | self.range | self.rate | self.mode);
                                    def reset(self):
                                        self.i2c.writeto_mem(QMC5883.ADDR, QMC5883.RESET, 0x01)
                                        time.sleep(0.1)
                                        self.reconfig()
                                        time.sleep(0.01)
                                    def setOversampling(self, x):
                                        self.oversampling = x
                                        self.reconfig()
                                    def setRange(x):
                                        self.range = x
                                        self.reconfig()
                                    def setSamplingRate(self, x):
                                        self.rate = x
                                        self.reconfig()
                                    def ready(self):
                                        status = self.i2c.readfrom_mem(QMC5883.ADDR, QMC5883.STATUS, 1)[0]
                                        # prevent hanging up here.
                                        # Happens when reading less bytes then then all 3 axis and will end up in a loop.
                                        # So, return any data but avoid the loop.
                                        if (status == QMC5883.STATUS_DOR):
                                            print("fail")
                                            return QMC5883.STATUS_DRDY
                                        return status & QMC5883.STATUS_DRDY
                                    def readRaw(self):
                                        while not self.ready():
                                            idle()
                                            pass
                                        # Python performs a wrong casting at read_i2c_block_data.
                                        # The filled buffer has to be onverted afterwards by mpdule Struct
                                        register = self.i2c.readfrom_mem(QMC5883.ADDR, QMC5883.X_LSB, 9);
                                        # Convert the axis values to signed Short before returning
                                        x, y, z, status, t = struct.unpack('<hhhBh', register)
                                        return (x, y, z, t)
                                and a short test code:
                                from qmc5883 import QMC5883
                                i2c=I2C()
                                print(i2c.scan())
                                time.sleep(1)
                                qmc = QMC5883(i2c)
                                    print(qmc.readRaw())
                                    time.sleep(1)
                                  tttadam @robert-hh
                                  @robert-hh thank you, it's looks useful, but after some time it's produce an OSError. Line 17 in my code is this : print(qmc.readRaw())
                                  and the line 99 is this. register = self.i2c.readfrom_mem(QMC5883.ADDR, QMC5883.X_LSB, 9)
                                  I think there were an ; which is not needed.
                                  But something else is still not alright. I didn't find it yet.
                                  (6967, -4882, -7620, -1943)
                                  (4742, -7337, -7950, -1923)
                                    File "main2.py", line 17, in <module>
                                    File "/flash/lib/qmc5883.py", line 99, in readRaw
                                  OSError: I2C bus error
                                    tttadam @robert-hh
                                    This is the error what i get now. Maybe tomorrow with fresh eye I will see something :)
                                    [13, 64, 104, 119]
                                    11001001
                                      File "/flash/lib/qmc5883.py", line 95, in readRaw
                                      File "/flash/lib/qmc5883.py", line 81, in ready
                                    • K Offline
                                      kuqizz
                                        robert-hh @tttadam
                                        @tttadam No, the ; is not needed (probably a left-over from an initial C-Code file), but it also does not hurt. There is another one in reconfig(). The OSError is probably caused by a I2C communication problem to the device. I did not let it run for longer than about 20 minutes or 1000 measurement. If you enclose that into a try/except clause, does the device recover?
                                        The temperature reading has an offset. That is also told in the data sheet. If I add 4900 to the value, it is almost OK. The value seems to be scaled as °C*100.
                                          tttadam @robert-hh
                                          @robert-hh Okay, So I try-catch block for OSError for
                                          and
                                          lines. Looks like it's not recovering.
                                          Something went wrongI2C bus error
                                            File "/flash/lib/qmc5883.py", line 110, in readRaw
                                            File "/flash/lib/qmc5883.py", line 97, in ready
                                          NameError: local variable referenced before assignment.
                                          Did you used this library for porting?
                                          Because it's mention something about readraw blocking.
                                          Where did you find the desription about these four values? What are does mean?
                                          The whole code looks like this, but it is the same, only thing I added, that I moved a i2c magic into the init method from main:
                                          import struct
                                          class QMC5883:
                                              ADDR = 0x0D
                                              X_LSB = 0
                                              X_MSB = 1
                                              Y_LSB = 2
                                              Y_MSB = 3
                                              Z_LSB = 4
                                              Z_MSB = 5
                                              STATUS = 6
                                              T_LSB = 7
                                              T_MSB = 8
                                              CONFIG = 9
                                              CONFIG2 = 10
                                              RESET = 11
                                              CHIP_ID = 13
                                              STATUS_DRDY = 1
                                              STATUS_OVL = 2
                                              STATUS_DOR = 4
                                                  self.i2c = i2c
                                                  self.i2c.writeto_mem(104, 107, 128) # reset MPU6050
                                                  self.i2c.writeto_mem(104, 107, 0) # disable sleep
                                                  self.i2c.writeto_mem(104, 55, 2)   # enable I2C passthru
                                                  self.reset()
                                              def reconfig(self):
                                              def reset(self):
                                                  time.sleep(0.1)
                                                  self.reconfig()
                                                  time.sleep(0.01)
                                                  self.reconfig()
                                              def setRange(x):
                                                  self.range = x
                                                  self.reconfig()
                                                  self.rate = x
                                                  self.reconfig()
                                              def ready(self):
                                                  try:
                                                  except OSError as e:
                                                      print("Something went wrong"+str(e))
                                                      #TODO: Tune it a little
                                                      print("fail")
                                                      try:
                                              def readRaw(self):
                                                      idle()
                                                      pass
                                                  return (x, y, z, t)
                                            robert-hh @tttadam
                                            @tttadam
                                            Thanks for the error log. But that only happens if you catch the error, print a message and then continue. The the symbol status is not defined, raising a new exception. So you would either add:
                                            status = 0
                                            or
                                            return 0
                                            after the print statements.
                                            No. I found Python code, which in turn might have been ported from that web side. See http://nobytes.blogspot.com/2018/03/qmc5883-magnetic-field-sensor.html with a link to another interesting port, of which I might carry over the calibration part.
                                            I did intentionally not include that I2C magic, because that is only relevant for this GY87 board.