    NTC temperature sensor
    sensorslopyadctemperaturentc
    26 Posts 6 Posters 15.4k Views 6 Watching
      robert-hh
      I think you could stil use the built-in ADC, if you requirement for precision is not extreme (like with 1% error). But you have to compensate the errors of the ADC.
      a) the zero point. look at which input voltage the output is different to zero. According to a comment below, this is somewhat like 0.1 V
      b) the scaling: Look at which input voltage the output just reaches the maximum value.
      c) nonlinearity. You could make a compensation table, or ignore it, if it is small enough and outside the range of interest.
      d) Noise
      a) and b) is easily compensated for. d) is reduced with taking an average of many samples, like you did. You do not have to wait a second between the samples. A few ms is sufficient, if at all, and a small capacitor like 10 nF with short leads directly at the ADC helps.
      Another observation: You connect the NTC to 3.2 V (are you sure it's not 3.3V?). The ADC max range is at 3.6 V, the reading at 3.2 V would be 3631. Instead of 4095, you should therefore use 3631 as the virtual maximum value. Then, the resistor value is 9793 (10412 for 3.3 V), which is 2% off the nominal value, and depending of the precision class of the resistor that could be the real value.
        tobru @robert-hh
        @robert-hh said in NTC temperature sensor:
        There is no exterme precision requirement. 1% would be completely fine.
        d) Noise
        a) and b) is easily compensated for. d) is reduced with taking an average of many samples, like you did. You do not have to wait a second in between, and a small capacitor like 10 nF with short leads directly at the ADC helps.
        Thanks for the inputs!
        It is connected to 3V3, so it is of course 3.3V. I've chosen 3.2V for Vin in the second equation because of the parameter attn=3. I've read that in this threads: https://forum.pycom.io/topic/226/lopy-adcs and here https://forum.pycom.io/topic/602/ntc-temperature-sensor/6
        Interesting. I must have missed this information in the documentation, I thought 3.3V is the maximum.
          robert-hh
          As always, the information given by espressif is poor. Nothing compared to the manuals issued for instance by Atmel, STM or Freescale. It is unclear, how much the attenuation level really is, some say 11db, some say 12 db. 11db would be a factor 3.55, 12 db a factor 3,98 (10**(atten/20)) of the base range, which is ?. In any case, better give it a try. If you have a voltage meter, get the value at the input and scale it by:
          Vrange = Vinput * (4095/reading)
            robert-hh
            So I gave it a try, connected a power source to the input and read the average of 100 samples each. The results are not convincing.
            a) Even at an average of 100 samples, there is a lot of noise..
            b) it looks pretty nonlinear., at least at attn 3
            results:
            attn = 3
            value 0 until 125 mV
            107	mV -> 0
            200	mV -> 95
            300	mV -> 215
            500	mV -> 455
            700	mV -> 700
            1000 mV -> 1070
            1500 mV -> 1700
            1600 mV -> 1815
            2000 mV -> 2310
            2500 mV -> 2930
            2900 mV -> 3540
            3000 mV -> 3740
            3100 mV -> 3955
            3170 mV -> 4095
            attn = 0
            Value 0 until 57 mV
            100 mV -> 127
            200 mV -> 550
            300 mV -> 974
            500 mV -> 1820
            700 mV -> 2650
            900 mV -> 3510
            1000 mV -> 3933
            1044 mV -> 4095
            If you look at that in a graph, at attn 3 the bends up beyond 2.5 V, while the attn=0 graph looks more linear, besides the 0-Offset.
            That's worse than I expected. The best one can get is to work with attn = 0 and use an external voltage divider.
            Edit: I found a link that shows an experience, which pretty much matches mine:
            http://www.esp32.com/viewtopic.php?t=1045
            The Figures I got are pretty much the same. So 6db attn would be an option too.
              jmarcelino @robert-hh
              @robert-hh
              this is an open issue on ESP-IDF and also the Arduino core
              https://github.com/espressif/esp-idf/issues/164
              https://github.com/espressif/arduino-esp32/issues/92
              The official response from Espressif is:
              The ADC frontend indeed has a non-linear response. Once characterization data is ready, we will take it into account inside ADC APIs, and update the datasheet with correct values of INL/DNL and effective resolution.
              So any efforts to compensate it at this stage will likely be rendered useless in a future update once the characterisation is complete (at least at ESP-IDF/MicroPython level)
              That's also why I suggested an external ADC for the time being, at least that won't change.
                robert-hh
                @jmarcelino: Yes, Ive read that. But you would still have to compensate for the non-zero range (at least in your circuit). So at the moment and with limited requirements for precision, using the lower attenuation variants 0 and 6db and simply adding an offset would be sufficient as compensation.
                If you need precise values, yes, then an external ADC is anyhow recommended.
                B.T.W. Is there still the option to use the ADC in 10 bit mode, like by an option res = xx in the channel set-up?
                • 1
                • 2