    Current sensor 15A SCT-013
    sensorcurrentlopy
    28 Posts 3 Posters 3.7k Views 3 Watching
    • V Offline
      Vicky_ @robert-hh
      @robert-hh Hello. The coding you shared, it works! Thanks a lot.
      I use it to measure a hairdryer rated 1000w to 1200w.
      when hairdryer is off I get 0.something.
      when I open level 1 I get 10. something.
      when I open level 2 I get 45. something.
      when I open level 3 I get 71. something.
      I chose the maximum value 71.something and divide 512 (9 bits ADC) times with 3.3v and 15A.
      eg:
      ((71.22/512)*3.3)*15 = 6.86A
      but the maximum current should be 1200/240v =5A, right?
      or my calculation is wrong?
      I used it to measure a phone charger but it has no different with when it is off, maybe the current is too small.
      once again, thanks
      alt text
        robert-hh @Vicky_
        @vicky_ The transfer ratio is hard to guess, because there are some unknown figures in between, like the transfer function of your sensor. That is 1Veff at 15A. So at 5 A it should deliver 0.333Veff. But i did never determine the remainder of the transfer function.
        What you should do is to take the current of the hairdryer with an known good Multimeter and determine a factor from that. The ESP32 ADC is non-linear, especially at 11 dB attenuation. But the mid range values should be OK. Using 6 dB attenuation the linearity is better. But then you'll need a different interface circuit.
        Yes, at low currents the ADC noise and the phase noise of the sampling steps in. If the time for reading a value is larger, you'll have somewhat less noise. This time should be a integer multiple of the wave period. For 50 Hz, a multiple of 20 is fine, for 60 Hz a multiple of 50. So taking a multiple of 100 is good for both frequencies.
        V 1 Reply Last reply Reply Quote 1
        • V Offline
          Vicky_ @robert-hh
          @robert-hh Thanks for your suggestion! I understand what you trying to say until this part "If the time for reading a value is larger, you'll have somewhat less noise. This time should be a integer multiple of the wave period. For 50 Hz, a multiple of 20 is fine, for 60 Hz a multiple of 50. So taking a multiple of 100 is good for both frequencies."
          do you mean that at the coding the time I should modify it
          time1 = time x 100 and all time change it to time1?
          sorry.
            robert-hh @Vicky_
            @vicky_ in my example, the time for reading is 1000 = 1000ms. If that is too slow, you may take any multiple of 100, like 100, 200, 300, .... instead. Besides that, you can freely select the total measuring time.
            • V Offline
              Vicky_ @robert-hh
              @robert-hh ok thank you so much!
                StefanoF @robert-hh
                sorry Robert, because this schema is different of schema di Vicky? 957fd326-fdd1-45bf-b8b6-0878191859ce-image.png ,,
                can you kindly let me know which schema I need used?
                Many thanks
                  robert-hh @StefanoF
                  @StefanoF They are identical in that they shift up the signal to be measured by Vdd/2. The difference:
                  • In my schematic the sensor is directly tied to GND, here it is tied to a virtual GND at Vdd/2 with a impedance at 50 Hz of about 30 Ohm.
                  • I added in my schematics overvoltage protection, which is missing here.
                  As long as there is no excess current you are try to measure, both will work. In case of a shortage in the sensed circuit, there is a high risk that the connected Pycom device will be damaged.
                  P.S.: To get a result for measuring, only C1, R1 and R2 are needed in my circuit. Everything else is for protection.
                    robert-hh @StefanoF
                    @StefanoF The schema in your post and the one of Vicky are identical, just differently sketched.
                      StefanoF @robert-hh
                        StefanoF @robert-hh
                        StefanoF 2 days ago
                        Hi ,
                        I've used this the electronic schema , I've in out 1.65 volt at empty, the sensor is at 15A (STC 013-015)
                        Can you kindly help me with easy code,
                        apin = adc.channel(pin='P13', attn=ADC.ATTN_11DB)
                        peakVoltage = float(0)
                        ACCurrtntValue = float(0)
                        for i in range(5):
                            peakVoltage += apin.voltage()
                            utime.sleep_ms(1)
                        peakVoltage = (peakVoltage / 5)
                        voltageVirtualValue = (peakVoltage / 1000)
                        print(round(voltageVirtualValue,2))
                        result 1.65
                        Many thanks
                          robert-hh @Vicky_
                            robert-hh @StefanoF
                            @StefanoF You code snippet calculates the average DC voltage at the input. But what you need is the amplitude of the 50 Hz (or 60 Hz) AC voltage. So you have to do some kind of frequency analysis for that frequency. The most simple algorithm for doing that is the so called goertzel algorithm. If you scroll back in this thread, you will find an example which I posted there. I used that and it works fine, except for very small currents. But that is not the problem of the algorithm, that caused by the noise of the ADC capture, both amplitude and phase noise.
                              StefanoF @robert-hh
                              Hi Robert,
                              I've used this my code e variabile ma è valido:
                              Thanks you
                              def readACCurrentValue():
                                  global RANGE_AMPS, ADJUST_VOLTAGE
                                  for i in range(5):
                                      utime.sleep_ms(1)
                                  voltageVirtualValue = round(peakVoltage / 1000,2) - 1.65
                                  if(math.fabs(voltageVirtualValue)>0.1):
                                      ACCurrtntValue = (math.fabs(voltageVirtualValue) * 15)   #15 A
                                  return round(ACCurrtntValue,2)
                                robert-hh @StefanoF
                                @StefanoF I think your code is not useful. It does not determine the value of the 50HZ AC component. Instead it calculate the average value of a 5ms time window somewhere in the 20ms period of a 50 Hz wave. For a given constant current you will get a largely varying output value, if you repeat the call several time non-synchronous with the mains frequency. And even is the value is in the synchronous case seemingly constant, it may be totally wrong.
                                I tried similar approaches, e.g. finding the highest and lowest value and then calculating the difference, like a Vpp determination. But that was not robust at all. The only robust approach was using a FFT approach, like the mentioned Goertzel algorithm.
                                  StefanoF @robert-hh
                                  Not exist a driver for this component , ex. EmonLib.h of arduino ?
                                  Many thanks
                                    robert-hh @StefanoF
                                    @StefanoF said in Current sensor 15A SCT-013:
                                    EmonLib.h, Emonlib.cpp
                                    I do not know a python implementation for that algorithm. As far as I understand is, if calculates the integral over the zero compensated voltage square. That can be done and may work for strong signals. I expect it to fail for small signals.
                                      robert-hh @StefanoF
                                      @StefanoF Here is another code, which uses plain vanilla calc instead of the goertzel algorithm. That is more robust to cumulating rounding errors. I have my doubts about that for goertzel. This also tries to cater for sampling jitter.
                                      import gc
                                      import math
                                      import array
                                      from utime import ticks_us, ticks_ms, ticks_diff, sleep_ms
                                      from machine import ADC, Timer, idle, enable_irq, disable_irq
                                      # acquire ADC values. The paramters of the constructor are:
                                      # 1. the mains frequency (number, typically 50 or 60)
                                      # 2. the time (ms) for one test period. time must be an integer
                                      #    multiple of frequency period duration and the sampling period
                                      #    being n * 50ms for 60Hz and n * 20ms for 50 Hz. A good value is 200
                                      # 3. the sampling period (ms). time must be an integer multiple
                                      #    of the sampling period. The default is 2.
                                      class Acquire:
                                          def __init__(self, freq=50, *, time=200, sample_rate=2):
                                              self.sample_rate = sample_rate
                                              self.samples = time // sample_rate
                                              self.adc = ADC(bits=12)
                                              self.freq = freq
                                              self.data = array.array("f", [0.0 for _ in range(self.samples)])
                                              pi_f = (2 * math.pi * freq * self.sample_rate) / 1000
                                              self.timestamp = array.array("L", [0 for _ in range(self.samples)])
                                          def start(self, pin):
                                              self.pin_adc = self.adc.channel(pin=pin, attn=ADC.ATTN_11DB)
                                              self.count = 0
                                              self.busy = True
                                              self.alarm = Timer.Alarm(self.read_adc, 0, ms=self.sample_rate, periodic=True)
                                          def stop(self):
                                              self.alarm.cancel()
                                          def read_adc(self, alarm):
                                              self.data[self.count] = self.pin_adc.value()
                                              self.timestamp[self.count] = ticks_us()
                                              self.count += 1
                                              if self.count >= self.samples:
                                                  self.alarm.cancel()
                                                  self.busy = False
                                          def result(self):
                                              while self.busy == True:
                                                  sleep_ms(self.sample_rate)
                                              # normalize the time stamps
                                              for _ in range(1, self.count):
                                                  self.timestamp[_] = ticks_diff(self.timestamp[_], self.timestamp[0])
                                              self.timestamp[0] = 0
                                              vsin = 0.0
                                              vcos = 0.0
                                              pi_f = (2 * math.pi * self.freq) / 1000000
                                              for _ in range(self.count):
                                                  vsin += self.data[_] * math.sin(self.timestamp[_] * pi_f)
                                                  vcos += self.data[_] * math.cos(self.timestamp[_] * pi_f)
                                              amplitude = math.sqrt(vsin * vsin + vcos * vcos) / self.count
                                              gc.collect() # avoids automatic gc during sampling
                                              return amplitude
                                          def reading(self, pin):
                                              self.start(pin)
                                              return self.result()
                                      def run():
                                          pin = "P13"
                                          freq = 50
                                          meas_time = 1000
                                          acq = Acquire(freq, time=meas_time)
                                          try:
                                              for _ in range(100):
                                                  value = acq.reading(pin)
                                                  print(value)
                                          except:
                                              pass
                                          acq.stop()
                                          print("Handler stopped")
                                      run()
                                        StefanoF @robert-hh
                                        @robert-hh said in Current sensor 15A SCT-013:
                                        Goertze
                                        Many thanks Robert,
                                        I am attaching a files at empty (1.65 volt setoff)
                                        how should I interpret it ?
                                        Goertze.py
                                          robert-hh @StefanoF
                                          @StefanoF I repeated the test with a real current set-up (variable 0..30V transformer and a 1 Ohm load resistor) and the attached script:
                                          at 0 current it outputs. 0.06 +/- 0.3
                                          at ~0.2 A it reports ~2.5
                                          at ~0.5A it reports ~6.9
                                          at 1 A it reports ~13.0
                                          at 2 A it reports ~26.0
                                          at 3 A it reports ~39.0
                                          at 4 A it reports ~52.0
                                          at 5 A it reports ~65
                                          at 6 A it reports ~78.2
                                          at 7A it reports ~92
                                          at 8 A it reports ~105
                                          at 9 A it reports ~118.7
                                          Then the fuse of the 5 A transformer supply tripped in and the load resistor got HOT. No fear. It is an extremely robust supply, used for teaching. And the load resistor is a 50W type with a short time overrating of 250W, surface temperature up to 275°C.
                                          So the values are good in a range from .2 A up. Lower current readings are noisy.
                                          import gc
                                          import math
                                          import array
                                          from utime import sleep_ms, sleep_us
                                          from machine import ADC, Timer, idle, enable_irq, disable_irq, Pin
                                          # 2. the sampling period (ms). The default is 2 ms.
                                          class Acquire:
                                              def __init__(self, freq=50, *, sample_period=2):
                                                  self.sample_period = sample_period
                                                  self.omega = 2.0 * math.pi * freq / (1000 / sample_period)
                                                  self.coeff = 2.0 * math.cos(self.omega)
                                                  self.adc = ADC(bits=9)
                                              def start(self, pin, time=200):
                                                  self.samples = time // self.sample_period
                                                  self.count = 0
                                                  self.busy = True
                                                  self.q1 = 0.0
                                                  self.q2 = 0.0
                                                  self.alarm = Timer.Alarm(self.read_adc, 0, ms=self.sample_period, periodic=True)
                                              def stop(self):
                                                  self.alarm.cancel()
                                                  self.q0 = self.pin_adc() + self.coeff * self.q1 - self.q2
                                                  self.q2 = self.q1
                                                  self.q1 = self.q0
                                                  self.count += 1
                                                      self.alarm.cancel()
                                                      self.busy = False
                                              def result(self):
                                                      sleep_ms(self.sample_period)
                                                  # amplitude = 2 * math.sqrt(self.q1 * self.q1 +
                                                  #                           self.q2 * self.q2 -
                                                  #                           self.q1 * self.q2 * self.coeff) / self.count
                                                  # if phase is required:
                                                  real = self.q1 - self.q2 * math.cos(self.omega)
                                                  imag = self.q2 * math.sin(self.omega)
                                                  amplitude = 2 * math.sqrt(real * real + imag * imag) / self.count
                                                  phase = math.atan2(real, imag)
                                                  return amplitude
                                              def reading(self, pin, time):
                                                  self.start(pin, time)
                                              acq = Acquire(50) # 50 Hz
                                              value = acq.reading("P13", 1000)
                                              print (value)
                                            robert-hh @StefanoF
                                            @StefanoF Just one question: