    Current sensor 15A SCT-013
    sensorcurrentlopy
    28 Posts 3 Posters 4.1k Views 3 Watching
      robert-hh @StefanoF
      @StefanoF The schema in your post and the one of Vicky are identical, just differently sketched.
        StefanoF @robert-hh
        @robert-hh Thanks for your suggestion!
          StefanoF @robert-hh
          StefanoF 2 days ago
          Hi ,
          I've used this the electronic schema , I've in out 1.65 volt at empty, the sensor is at 15A (STC 013-015)
          Can you kindly help me with easy code,
          apin = adc.channel(pin='P13', attn=ADC.ATTN_11DB)
          peakVoltage = float(0)
          ACCurrtntValue = float(0)
          for i in range(5):
              peakVoltage += apin.voltage()
              utime.sleep_ms(1)
          peakVoltage = (peakVoltage / 5)
          voltageVirtualValue = (peakVoltage / 1000)
          print(round(voltageVirtualValue,2))
          result 1.65
          Many thanks
            robert-hh @Vicky_
              robert-hh @StefanoF
              @StefanoF You code snippet calculates the average DC voltage at the input. But what you need is the amplitude of the 50 Hz (or 60 Hz) AC voltage. So you have to do some kind of frequency analysis for that frequency. The most simple algorithm for doing that is the so called goertzel algorithm. If you scroll back in this thread, you will find an example which I posted there. I used that and it works fine, except for very small currents. But that is not the problem of the algorithm, that caused by the noise of the ADC capture, both amplitude and phase noise.
                StefanoF @robert-hh
                Hi Robert,
                I've used this my code e variabile ma è valido:
                Thanks you
                def readACCurrentValue():
                    global RANGE_AMPS, ADJUST_VOLTAGE
                    for i in range(5):
                        utime.sleep_ms(1)
                    voltageVirtualValue = round(peakVoltage / 1000,2) - 1.65
                    if(math.fabs(voltageVirtualValue)>0.1):
                        ACCurrtntValue = (math.fabs(voltageVirtualValue) * 15)   #15 A
                    return round(ACCurrtntValue,2)
                  robert-hh @StefanoF
                  @StefanoF I think your code is not useful. It does not determine the value of the 50HZ AC component. Instead it calculate the average value of a 5ms time window somewhere in the 20ms period of a 50 Hz wave. For a given constant current you will get a largely varying output value, if you repeat the call several time non-synchronous with the mains frequency. And even is the value is in the synchronous case seemingly constant, it may be totally wrong.
                  I tried similar approaches, e.g. finding the highest and lowest value and then calculating the difference, like a Vpp determination. But that was not robust at all. The only robust approach was using a FFT approach, like the mentioned Goertzel algorithm.
                    StefanoF @robert-hh
                    Not exist a driver for this component , ex. EmonLib.h of arduino ?
                    Many thanks
                      robert-hh @StefanoF
                      @StefanoF said in Current sensor 15A SCT-013:
                      EmonLib.h, Emonlib.cpp
                      I do not know a python implementation for that algorithm. As far as I understand is, if calculates the integral over the zero compensated voltage square. That can be done and may work for strong signals. I expect it to fail for small signals.
                        robert-hh @StefanoF
                        @StefanoF Here is another code, which uses plain vanilla calc instead of the goertzel algorithm. That is more robust to cumulating rounding errors. I have my doubts about that for goertzel. This also tries to cater for sampling jitter.
                        import gc
                        import math
                        import array
                        from utime import ticks_us, ticks_ms, ticks_diff, sleep_ms
                        from machine import ADC, Timer, idle, enable_irq, disable_irq
                        # acquire ADC values. The paramters of the constructor are:
                        # 1. the mains frequency (number, typically 50 or 60)
                        # 2. the time (ms) for one test period. time must be an integer
                        #    multiple of frequency period duration and the sampling period
                        #    being n * 50ms for 60Hz and n * 20ms for 50 Hz. A good value is 200
                        # 3. the sampling period (ms). time must be an integer multiple
                        #    of the sampling period. The default is 2.
                        class Acquire:
                            def __init__(self, freq=50, *, time=200, sample_rate=2):
                                self.sample_rate = sample_rate
                                self.samples = time // sample_rate
                                self.adc = ADC(bits=12)
                                self.freq = freq
                                self.data = array.array("f", [0.0 for _ in range(self.samples)])
                                pi_f = (2 * math.pi * freq * self.sample_rate) / 1000
                                self.timestamp = array.array("L", [0 for _ in range(self.samples)])
                            def start(self, pin):
                                self.pin_adc = self.adc.channel(pin=pin, attn=ADC.ATTN_11DB)
                                self.count = 0
                                self.busy = True
                                self.alarm = Timer.Alarm(self.read_adc, 0, ms=self.sample_rate, periodic=True)
                            def stop(self):
                                self.alarm.cancel()
                            def read_adc(self, alarm):
                                self.data[self.count] = self.pin_adc.value()
                                self.timestamp[self.count] = ticks_us()
                                self.count += 1
                                if self.count >= self.samples:
                                    self.alarm.cancel()
                                    self.busy = False
                            def result(self):
                                while self.busy == True:
                                    sleep_ms(self.sample_rate)
                                # normalize the time stamps
                                for _ in range(1, self.count):
                                    self.timestamp[_] = ticks_diff(self.timestamp[_], self.timestamp[0])
                                self.timestamp[0] = 0
                                vsin = 0.0
                                vcos = 0.0
                                pi_f = (2 * math.pi * self.freq) / 1000000
                                for _ in range(self.count):
                                    vsin += self.data[_] * math.sin(self.timestamp[_] * pi_f)
                                    vcos += self.data[_] * math.cos(self.timestamp[_] * pi_f)
                                amplitude = math.sqrt(vsin * vsin + vcos * vcos) / self.count
                                gc.collect() # avoids automatic gc during sampling
                                return amplitude
                            def reading(self, pin):
                                self.start(pin)
                                return self.result()
                        def run():
                            pin = "P13"
                            freq = 50
                            meas_time = 1000
                            acq = Acquire(freq, time=meas_time)
                            try:
                                for _ in range(100):
                                    value = acq.reading(pin)
                                    print(value)
                            except:
                                pass
                            acq.stop()
                            print("Handler stopped")
                        run()
                          StefanoF @robert-hh
                          @robert-hh said in Current sensor 15A SCT-013:
                          Goertze
                          Many thanks Robert,
                          I am attaching a files at empty (1.65 volt setoff)
                          how should I interpret it ?
                          Goertze.py
                            robert-hh @StefanoF
                            @StefanoF I repeated the test with a real current set-up (variable 0..30V transformer and a 1 Ohm load resistor) and the attached script:
                            at 0 current it outputs. 0.06 +/- 0.3
                            at ~0.2 A it reports ~2.5
                            at ~0.5A it reports ~6.9
                            at 1 A it reports ~13.0
                            at 2 A it reports ~26.0
                            at 3 A it reports ~39.0
                            at 4 A it reports ~52.0
                            at 5 A it reports ~65
                            at 6 A it reports ~78.2
                            at 7A it reports ~92
                            at 8 A it reports ~105
                            at 9 A it reports ~118.7
                            Then the fuse of the 5 A transformer supply tripped in and the load resistor got HOT. No fear. It is an extremely robust supply, used for teaching. And the load resistor is a 50W type with a short time overrating of 250W, surface temperature up to 275°C.
                            So the values are good in a range from .2 A up. Lower current readings are noisy.
                            import gc
                            import math
                            import array
                            from utime import sleep_ms, sleep_us
                            from machine import ADC, Timer, idle, enable_irq, disable_irq, Pin
                            # 2. the sampling period (ms). The default is 2 ms.
                            class Acquire:
                                def __init__(self, freq=50, *, sample_period=2):
                                    self.sample_period = sample_period
                                    self.omega = 2.0 * math.pi * freq / (1000 / sample_period)
                                    self.coeff = 2.0 * math.cos(self.omega)
                                    self.adc = ADC(bits=9)
                                def start(self, pin, time=200):
                                    self.samples = time // self.sample_period
                                    self.count = 0
                                    self.busy = True
                                    self.q1 = 0.0
                                    self.q2 = 0.0
                                    self.alarm = Timer.Alarm(self.read_adc, 0, ms=self.sample_period, periodic=True)
                                def stop(self):
                                    self.alarm.cancel()
                                    self.q0 = self.pin_adc() + self.coeff * self.q1 - self.q2
                                    self.q2 = self.q1
                                    self.q1 = self.q0
                                    self.count += 1
                                        self.alarm.cancel()
                                        self.busy = False
                                def result(self):
                                        sleep_ms(self.sample_period)
                                    # amplitude = 2 * math.sqrt(self.q1 * self.q1 +
                                    #                           self.q2 * self.q2 -
                                    #                           self.q1 * self.q2 * self.coeff) / self.count
                                    # if phase is required:
                                    real = self.q1 - self.q2 * math.cos(self.omega)
                                    imag = self.q2 * math.sin(self.omega)
                                    amplitude = 2 * math.sqrt(real * real + imag * imag) / self.count
                                    phase = math.atan2(real, imag)
                                    return amplitude
                                def reading(self, pin, time):
                                    self.start(pin, time)
                                acq = Acquire(50) # 50 Hz
                                value = acq.reading("P13", 1000)
                                print (value)
                              robert-hh @StefanoF
                              @StefanoF Just one question:
                              are you living in a 50Hz or 60Hz mains region. For 60Hz you have to change the call to Acquire into Acquire(60).
                                StefanoF @robert-hh
                                I live in Italy 50 Hz, Thanks a lot
                                  robert-hh @StefanoF
                                  @StefanoF I made a few more tests with the most recent code I have posted (which is the initial goertzel code).
                                  a) test for phase jitter. Instead of reading the ADC, i just supplied a artificial 50Hz sine with an amplitude of 50 and an offset of range/2 into the algorithm. Result: constant 49.99993, which means that there is no phase jitter.
                                  b) I connected the interface network, but not the sensor. Result: Output values between 0.005 and 0.03. Since the output value of 1Veff is about 240, that is equivalent of ~60µVeff, or about 1 mA through the sensor.
                                  c) connect a battery with 1.5V to the input. Result: values of about 0.5 -> Noisy battery!
                                  d) connect the SCT013 with no current. Value of 0.04 +/- 0.03. That's about 160µVeff of 3 mA (or 0.5 W at 230V) through the sensor. So it looks as if the sensor picks up some noise, but still ok.
                                  e) Using an external ADC (mcp3201). Result: values of 0.05. Slightly worse than using the internal ADC.
                                  Lesson learned: I will stick with the initial solution. The challenge is to proper shield the interface network and the cable from picking up unwanted noise.
                                  • 2 / 2